    Confirm the serial network of devices are wired and configured to have the same
    baud rate, serial port settings (for example, 8N1), and protocol (Modbus).
    • Confirm each serial device has a unique unit identifier.
    • Confirm the serial network of devices are connected to the gateway meter’s serial
    communication port.
    • Confirm your gateway meter is communicating over Ethernet.
  2. Baracskai Attila

    Baracskai Attila Administrator

  3. Baracskai Attila

    Baracskai Attila Administrator

    Next Step
    - Install ION Setup v3.0 Software from Schneider Electric website
    - Start ION Setup.
  4. Baracskai Attila

    Baracskai Attila Administrator

    Open the Setup Assistant for your meter.
    -Navigate to Communications > Serial settings and select the tab for the
    communications port that the serial network is connected to.
    -Select Protocol and click Edit. The protocol selection screen appears.
    -Set the protocol to Modbus Master.
    -Navigate to Communications > Network settings and select the TCP/IP tab.
    -Select Modbus Gateway and click Edit. The Modbus gateway selection screen is
    displayed.
    - Select the communications port that the serial network is connected to (and you just
    set to use the Modbus master protocol) and click OK. The Modbus gateway
    connection is created.
    - Create an Ethernet gateway site to access the serial network of devices through your
    gateway meter.
  5. Baracskai Attila

    Baracskai Attila Administrator

  6. Baracskai Attila

    Baracskai Attila Administrator

    Password: 0

    upload_2017-9-14_15-9-12.png

    Attached Files:

  7. Baracskai Attila

    Baracskai Attila Administrator

  8. Baracskai Attila

    Baracskai Attila Administrator

  9. Baracskai Attila

    Baracskai Attila Administrator

  10. Baracskai Attila

    Baracskai Attila Administrator

  11. Baracskai Attila

    Baracskai Attila Administrator

Share This Page